KaiS wrote:It depends on one’s local power system and mainly the fusing concept, which widely varies.
Two examples:
In Germany 16 A is mandatory, as household fuses are 16 A.
In GB the cable’s wall plug contains an extra fuse, so 10 A is OK.
You select circuit breaker rating based on your installation wiring (that the CB has to protect from overcurrent) current ratings, not the other way around. So if you have a power circuit with 2.5 mm² cabling and 16 A outlets, then you put 16 A circuit breaker. But if there is an outlet on the same circuit that is rated for 10 A, you must use 10 A CB, despite the cable supports higher currents. For lighting it's common to use 1.5 mm² cabling and 10 A breakers.
The circuit breakers protect your wiring and your outlets, not your appliances and their power cords. Appliances are expected to be protected by their own fuses and breakers designed for their operating currents, be it in the UK, the US, the EU, or any other civilized part of the world.
This has little to do with appliance power cords, where you select the current capacity based on your appliance's power rating. So waedi is correct here, either of these cables has more than enough current capacity. Although I still don't see the necessity to replace the supplied power cable of the DPS-2.
And in UK the plug contains not an "extra" fuse: it's mandatory due to the "ring main circuit" design that allows for 32 A CB in the distribution box, but the outlets are rated for 13 A, so they act also as outlet protection devices.